0 members (), 359 guests, and 22 robots.
#96271 11/15/05 11:50 PM
cruzer Offline OP
I'm feeding a 480v fire pump,if I put a dissconnect after the meter do I still have to put the feed in concrete
Workgear for Electricians
#96272 11/16/05 09:37 AM
With the brief amount of information you've given us the answer is No. Need more details.
George Little
#96273 11/16/05 12:26 PM
Refresh my memory someone! Doesn't this disconnect have to be available to qualified personel only?
Larry
#96274 11/16/05 06:04 PM
cruzer Offline OP
The disconnect is 10" from meter.
#96275 11/16/05 06:08 PM
cruzer Offline OP
sorry the fire pump is 208v.It's 480 going to transformer.
#96276 11/16/05 06:21 PM
Ron Offline
695.6(A)&(B) seem to require concrete, 1 hour rated circuit protective system or within a 1 hour enclosure.
Ron
#96277 11/16/05 07:48 PM
For a job of this nature as an inspector or a contractor, I'd be looking at the plans that should be available with an engineer's seal on them.
George Little
#96278 11/18/05 09:00 PM
Definitely get the plans and engineer with you. I just finished installing a 480v fire station yesterday.
BTW, check for continuity. 480v bomb went off due to my boss forgetting to check for continuity on Phase C. Can we say kaboom? Thank goodness the fire station was disconnected and only a crimp barrel grenaded.
#96279 11/19/05 01:49 PM
The feed needs to be ahead of the Service Disconnectg and remote of other disconnects. What are you doing with the jockey pump???