480V FEEDS #96271
11/15/05 10:50 PM
11/15/05 10:50 PM
C
cruzer  Offline OP
Junior Member
Joined: Sep 2005
Posts: 8
I'm feeding a 480v fire pump,if I put a dissconnect after the meter do I still have to put the feed in concrete

2017 / 2014 NEC & Related Books and Study Guides
Re: 480V FEEDS #96272
11/16/05 08:37 AM
11/16/05 08:37 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
With the brief amount of information you've given us the answer is No. Need more details.


George Little
Re: 480V FEEDS #96273
11/16/05 11:26 AM
11/16/05 11:26 AM
D
dlhoule  Offline
Member
Joined: Apr 2005
Posts: 73
Saline, MI 48197
Refresh my memory someone! Doesn't this disconnect have to be available to qualified personel only?
Larry

Re: 480V FEEDS #96274
11/16/05 05:04 PM
11/16/05 05:04 PM
C
cruzer  Offline OP
Junior Member
Joined: Sep 2005
Posts: 8
The disconnect is 10" from meter.

Re: 480V FEEDS #96275
11/16/05 05:08 PM
11/16/05 05:08 PM
C
cruzer  Offline OP
Junior Member
Joined: Sep 2005
Posts: 8
sorry the fire pump is 208v.It's 480 going to transformer.

Re: 480V FEEDS #96276
11/16/05 05:21 PM
11/16/05 05:21 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
695.6(A)&(B) seem to require concrete, 1 hour rated circuit protective system or within a 1 hour enclosure.


Ron
Re: 480V FEEDS #96277
11/16/05 06:48 PM
11/16/05 06:48 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
For a job of this nature as an inspector or a contractor, I'd be looking at the plans that should be available with an engineer's seal on them.


George Little
Re: 480V FEEDS #96278
11/18/05 08:00 PM
11/18/05 08:00 PM
D
DSpanoudakis  Offline
Member
Joined: Aug 2005
Posts: 89
Astoria, Queens, N.Y.C.
Definitely get the plans and engineer with you. I just finished installing a 480v fire station yesterday.

BTW, check for continuity. 480v bomb went off due to my boss forgetting to check for continuity on Phase C. Can we say kaboom? Thank goodness the fire station was disconnected and only a crimp barrel grenaded.

Re: 480V FEEDS #96279
11/19/05 12:49 PM
11/19/05 12:49 PM
P
Paul O'Connell  Offline
Member
Joined: Jul 2005
Posts: 56
Allen Park, Mi. USA
The feed needs to be ahead of the Service Disconnectg and remote of other disconnects. What are you doing with the jockey pump???


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
244,052 Are you busy
181,045 Re: Forum
171,285 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 14 (0.009s) Memory: 0.9978 MB (Peak: 1.1665 MB) Zlib enabled. Server Time: 2018-02-22 14:38:11 UTC