That was a test Bob. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) I don't follow your code reference (240.21(D) ) but if this is a Service, and when I read the first post, I see that it is then the proper code reference would be 230.71 and Don's recommendation would be valid.
George Little
|
|
|
|
|
Joined: Feb 2002
Posts: 182
Member
|
"So the engineer has stated my change order request will not be approved. I am concerned about my liabilty in this issue due to not meeting the NEC. " You can not install equipment that does not meet code regardless of the change order. I think its the engineers problem to solve and work out the problem with the owner.
"This project has turned very bad due to some other issues with design oh which I am taking a beating due to the engineer's faults." You should not take a loss because of an error by the engineer. Had he got it right the first time you would have bid higher using the 600 kcm. He needs to step up and explain the facts to the owner.
|
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
I've changed my mind. If the utility company installs their own conductors either with their own people or subs the job out to a contractor and they are the utility company wires then the size is under the specs of the utility company. If the job is specified by the engineer or architech and the conductors are owned by the owner then it is under the NEC and I think the size and disconnecting means is under the local inspector's authority.
George Little
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
I can't speak for any PoCo but everyone I've dealt with absolutely demands that the customer build the infrastructure and then DEED IT OVER FREE to the PoCo. They always want to own every component right up to the main point of entry.
In my area the AHJ inspects the secondary raceways from the Poco. He does not inspect the conductors that go into that raceway. It is up to the Poco to 'get happy'. They're the ones calling the shot.
Don't even waste your time calculating these feeders. Until the Poco gets happy the owner gets no juice. They won't even land the wires on the XFMR. BTW, no EC is allowed to land those conductors at the XFMR, don't even dream of it.
Let the owner know what is what and make the Poco the heavy.
Tesla
|
|
|
|
|
Joined: Feb 2002
Posts: 182
Member
|
"The project engineer specified the laterals on plans. Later admitting that they resized the MDP during the design and forgot the increase the service laterals."
This sounds like the customer is the owner of the service and not the utility. I've never seen an engineer spec a job for the utility on his plans.
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Bob
In California it is a universal condition of service that the Poco owns -- total clear title -- the conductors as a condition of service.
Check the fine print. You'll find that boilerplate in all utilities. Why? The MPOE is the legal liability cross over point.
The print just doesn't matter.
BTW, the secondaries on the EE's print were almost certainly transcribed from the ulitities' print. The 'committment letter' is not typically shared with the field troops. Many electricians have never seen one since it will have been sent to the EE. He is expected to incorporate their requirements in his prints.
Now our buddy screwed up, maybe. The owner is trying to shirk the tab.
Make the Poco the heavy. Put it to them, what size conductors are now required?
BTW, our Poco has these values already posted to their 'book'. You might be surprised to find that they will not require any increase in conductor size. Generally the Pocos use undersized conductors relative to the NEC.
Simply put only the Poco calls the shot. No one else, and you're not getting around them. But their conductor sizing is normally quite favorable. Don't sweat it.
Tesla
|
|
|
|
|
Joined: Oct 2005
Posts: 9
OP
Junior Member
|
Hey guys thanks for the response's,
Just to clarify. Until recently here the PoCo's always supplied the lateral conductors in customer supplied conduit. Lately they seem to be trying to change this by way of offering metering at the xformer. Now when the project is metered at the transformer the customer must supply the lateral feeders.
Now once again, my question remains. If I install these laterals, am I bound by the NEC ?
If so isn't 4 sets of 350MCM cu ( 4-3" PVC conduts) insuffcent for a 1600 amp main breaker in the service disconnect as per NEC 230.42(B)? (Service is already set in place) I do not have load calculations on this project from the engineer.
Can someone define Specific Installations as referanced in 230.42?
The 1600 amp main does have an adjustable trip setting. Would it be acceptable to just turn down the trip setting to an accpetable level (less than 1200 amps) Whats to keep someone from turning it up in the future ?
Thanks Again
|
|
|
|
|
Joined: Sep 2003
Posts: 650
Member
|
http://www.mikeholt.com/cgi-bin/codeforum/ultimatebb.cgi?ubb=print_topic;f=11;t=000658 Discusses the meaning of "Specific Installations"
-Jon
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
I have never seen a meter mounted directly at a padmounted transformer.
Could you get us pictures?
You seem to be describing a most unusual service. The CT zone within the big switch box going unused, since a separate meter and CT can will now be mounted at the pad. I find that set up hard to imagine.
Utility side arrangements are outside the scope of the NEC. Period. Their control extends up until the customer's first disconnecting means.
The meter's location does not change that.
Since there is no national code to tell the Poco what to do, they call their own shot. Out west the industry has banded together to form EUSERC, a standards committee.
I would log on to the utility website and poke around.
Even better, place a phone call. If you install anything they don't accept....
BTW the AHJ and Poco have long ago decided the turf war. You can ask either as to where they draw the line.
Tesla
|
|
|
|
|
Joined: Aug 2002
Posts: 141
Member
|
This metering at the xfmr. is odd. Usually you have to have a CT metering compartment in your switchgear. You could offer to provide a termination compartment per USERC standards and pay the utility to install cables to that compartment, The termination compartment would be the designated point of service termination. The AHJ would only have jusidiction from there into the building. Some utilities get nervous about having too many sets of large conductors terminated on the xfmr. spades. If the pad settles the secondary bushings leak because they are supported by the cables. Sometimes those utilities require a termination vault near the xfmr.
|
|
|
Posts: 57
Joined: August 2003
|
|
|
|