ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 703 guests, and 46 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#95927 10/22/05 09:10 PM
Joined: Sep 2001
Posts: 806
N
Member
I was taking one of my classes for my 34 hr. CEUs today, and a question came up that had the class and instructor stumped.

One of the guys was red-tagged by an inspector on a service installation using PVC conduit on the driveway side of a house. He used Sch. 80 pipe, with an LB below the meter pan to penetrate the wall into the panel.

Inspector claimed that the LB was subject to damage because it wasn't Schedule 80 rated.

Are heavy schedule PVC conduit bodies even manufactured?

Horizontal Ad
Joined: May 2005
Posts: 706
T
Member
I don't know, but he could go with metal to comply.

Dave

Joined: Mar 2005
Posts: 399
A
Member
You need to contact the manufacturer. Most claim that the reinforcing in the LBs creates a strength comparable to Sch. 80 conduit.
In my experience I have seen Sch. 40 conduit fail but have yet to see an LB broken.
Be carfull about using a metal LB if it is connected to PVC at both ends and has service conductors, because you now have to bond the LB.
Alan--Inspector.


Alan--
If it was easy, anyone could do it.
Joined: Jun 2005
Posts: 821
S
Member
I did a service like this this week. I used schedule 80 on the load side from the meter to the disco and lb'ed into a sweep and then into the panel. What I didn't do, though, was show the lettering on the schedule 80 to prove to the inspector that it was used. Do you think the inspector will fail the job?

Joined: Mar 2001
Posts: 333
S
Member
ShockMe77, if you used a PVC LB, pull the cover off the LB, the end of the pipe is probably visible and the wall thickness can be seen.

steve


Steve
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Can't say I ever seen/found a Sch 80 condulet, MA/FA/Cplg, etc.

Had the same thought, "should be same sch as conduit???".......called Carlon, had a chuckle. Guy said something to the effect of Alan Nadon's comments.

John


John

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Top Posters(30 Days)
Popular Topics(Views)
558,663 Are you busy
432,946 Re: Forum
401,943 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5