#95927 - 10/22/05 10:10 PM PVC conduit body schedule?  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
I was taking one of my classes for my 34 hr. CEUs today, and a question came up that had the class and instructor stumped.

One of the guys was red-tagged by an inspector on a service installation using PVC conduit on the driveway side of a house. He used Sch. 80 pipe, with an LB below the meter pan to penetrate the wall into the panel.

Inspector claimed that the LB was subject to damage because it wasn't Schedule 80 rated.

Are heavy schedule PVC conduit bodies even manufactured?


2017 / 2014 NEC & Related Books and Study Guides

#95928 - 10/23/05 11:36 AM Re: PVC conduit body schedule?  
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
I don't know, but he could go with metal to comply.

Dave


#95929 - 10/23/05 01:39 PM Re: PVC conduit body schedule?  
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
You need to contact the manufacturer. Most claim that the reinforcing in the LBs creates a strength comparable to Sch. 80 conduit.
In my experience I have seen Sch. 40 conduit fail but have yet to see an LB broken.
Be carfull about using a metal LB if it is connected to PVC at both ends and has service conductors, because you now have to bond the LB.
Alan--Inspector.


Alan--
If it was easy, anyone could do it.

#95930 - 10/30/05 09:06 PM Re: PVC conduit body schedule?  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
I did a service like this this week. I used schedule 80 on the load side from the meter to the disco and lb'ed into a sweep and then into the panel. What I didn't do, though, was show the lettering on the schedule 80 to prove to the inspector that it was used. Do you think the inspector will fail the job?


#95931 - 10/30/05 09:11 PM Re: PVC conduit body schedule?  
stamcon  Offline
Member
Joined: Mar 2001
Posts: 329
So San Francisco CA
ShockMe77, if you used a PVC LB, pull the cover off the LB, the end of the pipe is probably visible and the wall thickness can be seen.

steve


#95932 - 10/31/05 10:07 PM Re: PVC conduit body schedule?  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Can't say I ever seen/found a Sch 80 condulet, MA/FA/Cplg, etc.

Had the same thought, "should be same sch as conduit???".......called Carlon, had a chuckle. Guy said something to the effect of Alan Nadon's comments.

John


John


Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 