#95845 - 10/12/05 10:54 PM grounding  
cruzer  Offline
Junior Member
Joined: Sep 2005
Posts: 8
question can you use more than one ground on a ground clamp on the water pipe,does the ground pipe have to be bonded.


2017 / 2014 NEC & Related Books and Study Guides

#95846 - 10/13/05 04:30 AM Re: grounding  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Any wire terminal has to be listed for use with more than one conductor if you want to use it that way.

I have not seen ground clamps listed for more than one conductor.

Quote
does the ground pipe have to be bonded


If you mean does a metal raceway enclosing a grounding electrode conductor need to be bonded the answer is yes it does need to be bonded at each end.


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7434 MB (Peak: 0.8618 MB) Zlib enabled. Server Time: 2017-12-12 20:03:22 UTC