Posted By: cruzer grounding - 10/13/05 03:54 AM
question can you use more than one ground on a ground clamp on the water pipe,does the ground pipe have to be bonded.
Posted By: iwire Re: grounding - 10/13/05 09:30 AM
Any wire terminal has to be listed for use with more than one conductor if you want to use it that way.

I have not seen ground clamps listed for more than one conductor.

Quote
does the ground pipe have to be bonded

If you mean does a metal raceway enclosing a grounding electrode conductor need to be bonded the answer is yes it does need to be bonded at each end.