#95637 09/23/05 07:54 PM
BigJohn Offline OP
Just want to double check:
Is it legal to put connectors inside a j-box (i.e., the locknut on the outside)? 314.16(B)(2) seems to say yes.
Is it legal to install Romex in boxes and light fixtures without connectors (only use bushings)? 314.17(C)Exception says only on single-gang non-metallic boxes. What about multi-gang fiberglass boxes that have no provisions for clamps?
When fluorescent fixtures are mounted overtop of junction boxes, is that box considered inaccessible? 314.29 seems ambiguous. A keyless fixture obviously wouldn't be "part of the building," is a fluorescent?
Thanks.
-John
#95638 09/23/05 09:32 PM
If you turn the connector around you would need a "clamp" deduction in the fill (IMHO)
A luminaire is not part of the building finish.
#95639 09/23/05 10:53 PM
Connectors need to be installed with the clamping means external to the box to be installed per the listing and labeling. The do make snap in non-metallic clamps that can be installed from inside the box for situations where you don't have access to the exterior of the box.
You are required to secure the cable to the box per the last sentence od 314.17(C). The exception is for 1 gang boxes where you are able to secure the cable within 8" of the box measured along the cable.
I have not seen a "Listed" multigang NM cable box that didn't have clamps. Possibly I'm in need of an update [Linked Image]
As for the box behind the fluorescent fixture look at 410.14(B)
George Little
#95640 09/23/05 11:12 PM
originally .posted by Big John
Yes 314.16 (B)(2) a single volume allowance in accordance with Table 314.16(B) shall be made based on the largest conductor present in the box.
the cable MUST be secured to the box or piece of equipment
314.17 (C) In all instances, all permitted wiring methods shall be secured to the boxes.
300.15(E). (E) Integral Enclosure. A wiring device with integral enclosure identified for the use, having brackets that securely fasten the device to walls or ceilings of conventional on-site frame construction, for use with nonmetallic-sheathed cable, shall be permitted in lieu of a box or conduit body.
Yes, 410.14 (B) Access to Boxes. Electric-discharge luminaires (fixtures) surface mounted over concealed outlet, pull, or junction boxes and designed not to be supported solely by the outlet box shall be provided with suitable openings in the back of the luminaire (fixture) to provide access to the wiring in the box.
Mike
#95641 09/23/05 11:13 PM
I may be in the backwaters of the world but I have not seen a flourecent fixture with a big hole in the back. Do they make them?
#95642 09/23/05 11:49 PM
There is often a 2" or so KO in the center of the back. I think 2" is a little small to access the box and I haven't seen a fixture with a bushing, to cover the sheet metal edges of the hole(I think they ought to include one).
steve
Steve
#95643 09/24/05 01:14 AM
That sounds like a circular razor blade. How can that be legal?
#95644 09/24/05 01:24 PM
Not if you use one of these
[Linked Image from bptfittings.com]
[This message has been edited by jw electric (edited 09-24-2005).]
Mike
#95645 09/24/05 03:47 PM
cool.
To be honest I have never seen a box behind a flourecent. They always feed the wiring method directly into the fixture and use it for the box.
#95646 09/24/05 06:14 PM
BigJohn Offline OP
Just some clarification: "Electric Discharge Luminaire," when I read that I assumed it meant for HID lighting like HPS or mercury vapor. Are fluorescents just low-pressure electric discharge?
Per 314.17, I don't think it is.
If I don't have some sort of bushing, my solution is to cut an X in the back of the fixture and fold the triangles of metal back, so you have a square hole with rounded edges.
But since that takes more time than simply pulling through the 2" k/o, I've been getting heat about it, which is why I was looking for the Code references that y'all supplied [Linked Image] to back me up.
Thanks for the help.
-John
Edited to clarify.
[This message has been edited by BigJohn (edited 09-25-2005).]
