pool codes #95332
09/07/05 09:18 PM
09/07/05 09:18 PM
M
MI Sparky  Offline OP
Member
Joined: Jul 2005
Posts: 14
Fenton, MI
680.42 states: OUTDOOR INSTALLATIONS A spa or hot tub installed outdoors shall comply with the provisions of Parts I and II of this article, except as permitted in 680.42(A) and (B), that would otherwise apply to pools installed outdoors.

680.22(3) is the reference to the plug I am talking about

Now the question: I just got knocked down for a hot tub that was installed on a concrete porch that the required outdoor plug (installed 12 years ago) was 7 feet from and GFI'd. This should or should not be grandfathered? The plug is in brick. The basement is finished.


I thought that was off!!!!
2017 / 2014 NEC & Related Books and Study Guides
Re: pool codes #95333
09/07/05 10:57 PM
09/07/05 10:57 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
Can you make this work?
680.22 Area Lighting, Receptacles, and Equipment.
(A) Receptacles.
(1) Circulation and Sanitation System, Location. Receptacles that provide power for water-pump motors or for other loads directly related to the circulation and sanitation system shall be located at least 3.0 m (10 ft) from the inside walls of the pool, or not less than 1.5 m (5 ft) from the inside walls of the pool if they meet all of the following conditions:
(1) Consist of single receptacles
(2) Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection


or
(4) Restricted Space. Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot preclude meeting the required clearances, not more than one receptacle outlet shall be permitted if not less than 1.5 m (5 ft) measured horizontally from the inside wall of the pool.

[This message has been edited by gfretwell (edited 09-07-2005).]


Greg Fretwell
Re: pool codes #95334
09/07/05 11:12 PM
09/07/05 11:12 PM
M
MI Sparky  Offline OP
Member
Joined: Jul 2005
Posts: 14
Fenton, MI
nope, (4) doesnt apply because beyond the doorwall is about 4 feet of space. The problem I have is the failure of the existing plug.

Inspector said "why dont you tear out the inside plug (finished basement) and drill through the brick and add a plug?"


I thought that was off!!!!
Re: pool codes #95335
09/07/05 11:24 PM
09/07/05 11:24 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
Move the hot tub? [Linked Image]


Greg Fretwell
Re: pool codes #95336
09/07/05 11:27 PM
09/07/05 11:27 PM
M
MI Sparky  Offline OP
Member
Joined: Jul 2005
Posts: 14
Fenton, MI
lol I wish, it was a brand new concrete pour for it. Right against the house...about 10 feet from the doorwall.


I thought that was off!!!!
Re: pool codes #95337
09/08/05 08:17 AM
09/08/05 08:17 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Sure the outlet is grandfathered in but the new tub is not.

He is not failing the outlet for being to close to the tub.

He is failing the tub for being to close to the outlet.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: pool codes #95338
09/08/05 11:37 AM
09/08/05 11:37 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
If you can't get in under the restricted space rule I suspect you are scrod.
The AHJ is the final word unless you want to stir the pot.

How far is "about 10'"?

Bear in mind that rule doesn't say it has to be 9'11" away (or whatever the fartherest distance available) if you can't get >10'. If you can't get >10' it can be 5.0001'.


Greg Fretwell
Re: pool codes #95339
09/08/05 11:43 PM
09/08/05 11:43 PM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
Can you mount an extension to the existing box then pipe over three feet and mount a GFCI in a surface mounted box?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 9
Popular Topics(Views)
249,313 Are you busy
187,255 Re: Forum
176,613 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9936 MB (Peak: 1.1529 MB) Zlib enabled. Server Time: 2018-09-20 22:22:09 UTC