1 members (Scott35), 534 guests, and 31 robots.
#95279 09/06/05 07:00 PM
jes Offline OP
15 Amp, 125 volt branch circuit with duplex 15 Amp, 125 volt receptacles. Plugged into a single duplex are two 6.5 Amp (nameplate) commercial referigerators, one into each position. For the sake of discussion there are no other loads. Does this violate ANY ratings or NEC requirements?
#95280 09/06/05 07:14 PM
I would say no.
I believe a refrigerator is not a continuous load ( on for 3 or more hours). The compressor will cycle on and off but should not run continuous.
#95281 09/06/05 08:27 PM
210.21(B)(2)
If the "duplex" receptacle is considered 2 receptacles, (and I believe it is) you would have a violation.
#95282 09/06/05 08:42 PM
Redsy, since this is in fact two receptacles, neither one would be loaded to the maximum limit of Table 210.21(B)(2) for a 15 amp receptacle.
Roger
#95283 09/06/05 09:24 PM
OK, so it's per each receptacle?
#95284 09/06/05 10:40 PM
No overload, no violation but poor design. Just a matter of time before both units start at the same time and that could spell problem.
George Little
#95285 09/08/05 05:27 AM
jes Offline OP
And no argument...
To change the question slightly...
Suppose the duplex were split and each receptacle had it's own 15 Amp circuit.
A load of 12 Amps could be connected to each, giving a total current of 24 amps through a standard, everyday, less than $1, duplex receptacle, correct?
#95286 09/08/05 06:50 AM
Yes that is correct.
Now how long would that cheap receptacle would last is another question altogether.
