15 Amp, 125 volt branch circuit with duplex 15 Amp, 125 volt receptacles. Plugged into a single duplex are two 6.5 Amp (nameplate) commercial referigerators, one into each position. For the sake of discussion there are no other loads. Does this violate ANY ratings or NEC requirements?
|
|
|
|
Joined: Jan 2005
Posts: 316
Member
|
I would say no. I believe a refrigerator is not a continuous load ( on for 3 or more hours). The compressor will cycle on and off but should not run continuous.
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
210.21(B)(2) If the "duplex" receptacle is considered 2 receptacles, (and I believe it is) you would have a violation.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Redsy, since this is in fact two receptacles, neither one would be loaded to the maximum limit of Table 210.21(B)(2) for a 15 amp receptacle.
Roger
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
OK, so it's per each receptacle?
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
No overload, no violation but poor design. Just a matter of time before both units start at the same time and that could spell problem.
George Little
|
|
|
|
Joined: Jul 2002
Posts: 103
OP
Member
|
And no argument...
To change the question slightly... Suppose the duplex were split and each receptacle had it's own 15 Amp circuit. A load of 12 Amps could be connected to each, giving a total current of 24 amps through a standard, everyday, less than $1, duplex receptacle, correct?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Yes that is correct.
Now how long would that cheap receptacle would last is another question altogether.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 5,445
Joined: January 2005
|
|
|
|
|