#95279 09/06/05 07:00 PM
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
15 Amp, 125 volt branch circuit with duplex 15 Amp, 125 volt receptacles. Plugged into a single duplex are two 6.5 Amp (nameplate) commercial referigerators, one into each position. For the sake of discussion there are no other loads. Does this violate ANY ratings or NEC requirements?

Horizontal Ad
#95280 09/06/05 07:14 PM
Joined: Jan 2005
Posts: 316
L
Member
I would say no.
I believe a refrigerator is not a continuous load ( on for 3 or more hours). The compressor will cycle on and off but should not run continuous.

#95281 09/06/05 08:27 PM
Joined: Mar 2001
Posts: 2,056
R
Member
210.21(B)(2)
If the "duplex" receptacle is considered 2 receptacles, (and I believe it is) you would have a violation.

#95282 09/06/05 08:42 PM
Joined: May 2002
Posts: 1,716
R
Member
Redsy, since this is in fact two receptacles, neither one would be loaded to the maximum limit of Table 210.21(B)(2) for a 15 amp receptacle.

Roger

#95283 09/06/05 09:24 PM
Joined: Mar 2001
Posts: 2,056
R
Member
OK, so it's per each receptacle?

#95284 09/06/05 10:40 PM
Joined: Jan 2004
Posts: 1,507
G
Member
No overload, no violation but poor design. Just a matter of time before both units start at the same time and that could spell problem.


George Little
#95285 09/08/05 05:27 AM
Joined: Jul 2002
Posts: 103
J
jes Offline OP
Member
And no argument...

To change the question slightly...
Suppose the duplex were split and each receptacle had it's own 15 Amp circuit.
A load of 12 Amps could be connected to each, giving a total current of 24 amps through a standard, everyday, less than $1, duplex receptacle, correct?

#95286 09/08/05 06:50 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Yes that is correct.

Now how long would that cheap receptacle would last is another question altogether.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Link Copied to Clipboard
Advertisement:-Right

* * * * * * *
Tools for Electricians
Tools for Electricians
 
* * * * * * *

2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Popular Topics(Views)
323,671 Are you busy
247,971 Re: Forum
231,748 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5