#8 bonding wire #94574
08/01/05 03:12 PM
08/01/05 03:12 PM
E
Edward  Offline OP
Member
Joined: Dec 2002
Posts: 308
California
Does the #8 solid ground that is used to bond the metallic frames of electric motors and associated parts of an indoor jacuzzi have to go back to the panel?

Or can it be bonded to the water supply to the jacuzzi?

I think it is the first option but i am not sure.
Thanks
Edward.


Thanks
Edward
2017 / 2014 NEC & Related Books and Study Guides
Re: #8 bonding wire #94575
08/01/05 04:52 PM
08/01/05 04:52 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
It does not have to go back to the panel. You are just bonding all of the metallic parts together. You must connect the water lines to this. It is not optional.

Re: #8 bonding wire #94576
08/01/05 05:00 PM
08/01/05 05:00 PM
E
Edward  Offline OP
Member
Joined: Dec 2002
Posts: 308
California
thank you


Thanks
Edward
Re: #8 bonding wire #94577
08/02/05 09:15 PM
08/02/05 09:15 PM
F
foestauf  Offline
Member
Joined: Aug 2005
Posts: 49
Florida
A guy other day was complaining to me that his inspector required him to run it back to panel.

Re: #8 bonding wire #94578
08/02/05 11:15 PM
08/02/05 11:15 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,225
Estero,Fl,usa
680.26 Bonding.
(A) Performance. The bonding required by this section shall be installed to eliminate voltage gradients in the pool area as prescribed.
FPN:This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,236
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,901 Are you busy
184,248 Re: Forum
173,489 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9663 MB (Peak: 1.1047 MB) Zlib enabled. Server Time: 2018-05-25 07:17:40 UTC