#94574 - 08/01/05 03:12 PM #8 bonding wire  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
Does the #8 solid ground that is used to bond the metallic frames of electric motors and associated parts of an indoor jacuzzi have to go back to the panel?

Or can it be bonded to the water supply to the jacuzzi?

I think it is the first option but i am not sure.
Thanks
Edward.


Thanks
Edward

2017 / 2014 NEC & Related Books and Study Guides

#94575 - 08/01/05 04:52 PM Re: #8 bonding wire  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
It does not have to go back to the panel. You are just bonding all of the metallic parts together. You must connect the water lines to this. It is not optional.


#94576 - 08/01/05 05:00 PM Re: #8 bonding wire  
Edward  Offline
Member
Joined: Dec 2002
Posts: 308
California
thank you


Thanks
Edward

#94577 - 08/02/05 09:15 PM Re: #8 bonding wire  
foestauf  Offline
Member
Joined: Aug 2005
Posts: 49
Florida
A guy other day was complaining to me that his inspector required him to run it back to panel.


#94578 - 08/02/05 11:15 PM Re: #8 bonding wire  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,120
Estero,Fl,usa
680.26 Bonding.
(A) Performance. The bonding required by this section shall be installed to eliminate voltage gradients in the pool area as prescribed.
FPN:This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode.


Greg Fretwell


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 