#94574 08/01/05 02:12 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Does the #8 solid ground that is used to bond the metallic frames of electric motors and associated parts of an indoor jacuzzi have to go back to the panel?

Or can it be bonded to the water supply to the jacuzzi?

I think it is the first option but i am not sure.
Thanks
Edward.


Thanks
Edward
Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#94575 08/01/05 03:52 PM
Joined: Jan 2002
Posts: 1,457
E
Member
It does not have to go back to the panel. You are just bonding all of the metallic parts together. You must connect the water lines to this. It is not optional.

#94576 08/01/05 04:00 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
thank you


Thanks
Edward
#94577 08/02/05 08:15 PM
Joined: Aug 2005
Posts: 49
F
Member
A guy other day was complaining to me that his inspector required him to run it back to panel.

#94578 08/02/05 10:15 PM
Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
680.26 Bonding.
(A) Performance. The bonding required by this section shall be installed to eliminate voltage gradients in the pool area as prescribed.
FPN:This section does not require that the 8 AWG or larger solid copper bonding conductor be extended or attached to any remote panelboard, service equipment, or any electrode.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
BigB 8
triple 3
Popular Topics(Views)
302,637 Are you busy
231,939 Re: Forum
216,588 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5