0 members (), 197 guests, and 33 robots.
For a laboratory space, we are required to put safety showers with a pull chain adjacent to the exit door. What NEC requirements are there for light switches and receptacles? Thanks. Andrew
I should have put, "What NEC requirements are there for light switches and receptacles within the safety shower area, and what distance is the safety shower area?"
How about
I. Installation
312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6 mm (1/4 in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof.
Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.
OR
404.4 Wet Locations.
A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
[This message has been edited by gfretwell (edited 07-13-2005).]