Joined: Apr 2005
Posts: 3
A
Junior Member
For a laboratory space, we are required to put safety showers with a pull chain adjacent to the exit door. What NEC requirements are there for light switches and receptacles? Thanks. Andrew

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Apr 2005
Posts: 3
A
Junior Member
I should have put, "What NEC requirements are there for light switches and receptacles within the safety shower area, and what distance is the safety shower area?"

Joined: Jul 2004
Posts: 9,719
Likes: 11
G
Member
How about

I. Installation
312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6 mm (1/4 in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof.
Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.

OR

404.4 Wet Locations.
A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

[This message has been edited by gfretwell (edited 07-13-2005).]


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
295,186 Are you busy
226,767 Re: Forum
211,914 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5