Safety Showers and Light Switches #94173 07/13/05 11:22 AM
Joined: Apr 2005
Posts: 3
A
ayakimov Offline OP
Junior Member
For a laboratory space, we are required to put safety showers with a pull chain adjacent to the exit door. What NEC requirements are there for light switches and receptacles? Thanks. Andrew

2017 / 2014 NEC & Related Books and Study Guides
Re: Safety Showers and Light Switches #94174 07/13/05 11:26 AM
Joined: Apr 2005
Posts: 3
A
ayakimov Offline OP
Junior Member
I should have put, "What NEC requirements are there for light switches and receptacles within the safety shower area, and what distance is the safety shower area?"

Re: Safety Showers and Light Switches #94175 07/13/05 12:37 PM
Joined: Jul 2004
Posts: 9,408
G
gfretwell Offline
Member
How about

I. Installation
312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6 mm (1/4 in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof.
Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.

OR

404.4 Wet Locations.
A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

[This message has been edited by gfretwell (edited 07-13-2005).]


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,540 Are you busy
194,935 Re: Forum
184,367 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3