50 amp hot tub #94070 07/05/05 10:33 PM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
can you use nm 8-3 to feed a 50 amp hot tub?

2017 / 2014 NEC & Related Books and Study Guides
Re: 50 amp hot tub #94071 07/05/05 11:21 PM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
I think not. NM is not one of the approved wiring methods in 680 part II. I also could have problems with the ampacity, based on the nameplate rating of the spa and mfg instructions. 8ga is only good for 40a in the 60c column.


Greg Fretwell
Re: 50 amp hot tub #94072 07/06/05 06:16 AM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline
Member
Greg- The question is not stating whether it is an indoor or outdoor spa. 680.42 and 680.43 come into play here.


George Little
Re: 50 amp hot tub #94073 07/06/05 08:30 AM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
it is an outdoor hot tub

Re: 50 amp hot tub #94074 07/06/05 03:44 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
Are you asking if you can run NM outside to a hot tub?

Re: 50 amp hot tub #94075 07/06/05 04:59 PM
Joined: Jun 2004
Posts: 610
S
shortcircuit Offline
Member
Romex (type NM) is allowed in the interior of a one family dwelling or the interior of a structure associated with a one family dwelling...

But read the instructions with the tub and labels at the control box behind the skirt of the tub. Some require a full size EGC to be run with the circuit conductors...

shortcircuit

Re: 50 amp hot tub #94076 07/06/05 05:25 PM
Joined: Feb 2005
Posts: 44
B
boggerbutt2454 Offline
Member
Shorties right read your Manufacture's manual most spa manufacture's will put min. wire size and I've found more times tahn not it is a #6 copper, but check your manual. If customer doesn' know call dealer they bought it from.

Re: 50 amp hot tub #94077 07/06/05 05:38 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
If NM is in fact appropriate 8 AWG NM can not be used above 40 amps.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 50 amp hot tub #94078 07/07/05 01:22 AM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
no i am not asking if i can run the nm outside. just wondering if i can calculate hot tub as a motor to use smaller wire.

any thoughts against using 6-3 aluminum?

Re: 50 amp hot tub #94079 07/07/05 11:52 AM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
A spa is a combination load with a significant part that is a "toaster wire" heater. The answer is in the manufacturer's instructions unless you want to start reading nameplate ratings and calculating.
You are still stuck in the 60c column with Romex.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
Trumpy 1
Popular Topics(Views)
260,697 Are you busy
195,725 Re: Forum
185,108 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3