can you use nm 8-3 to feed a 50 amp hot tub?
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I think not. NM is not one of the approved wiring methods in 680 part II. I also could have problems with the ampacity, based on the nameplate rating of the spa and mfg instructions. 8ga is only good for 40a in the 60c column.
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Greg- The question is not stating whether it is an indoor or outdoor spa. 680.42 and 680.43 come into play here.
George Little
|
|
|
|
Joined: Mar 2005
Posts: 240
OP
Member
|
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Are you asking if you can run NM outside to a hot tub?
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Romex (type NM) is allowed in the interior of a one family dwelling or the interior of a structure associated with a one family dwelling...
But read the instructions with the tub and labels at the control box behind the skirt of the tub. Some require a full size EGC to be run with the circuit conductors...
shortcircuit
|
|
|
|
Joined: Feb 2005
Posts: 44
Member
|
Shorties right read your Manufacture's manual most spa manufacture's will put min. wire size and I've found more times tahn not it is a #6 copper, but check your manual. If customer doesn' know call dealer they bought it from.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
If NM is in fact appropriate 8 AWG NM can not be used above 40 amps.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2005
Posts: 240
OP
Member
|
no i am not asking if i can run the nm outside. just wondering if i can calculate hot tub as a motor to use smaller wire.
any thoughts against using 6-3 aluminum?
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
A spa is a combination load with a significant part that is a "toaster wire" heater. The answer is in the manufacturer's instructions unless you want to start reading nameplate ratings and calculating. You are still stuck in the 60c column with Romex.