If a non-metalic handhole has a metalic cover, is it required to be bonded according to 2005 NEC?
shortcircuit
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Been in a lot of them Utility and Privitely owned Have never seen one Bonded to date.
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
See 314.29(D) Covers. Handhole enclosure covers shall have an identifying mark or logo that prominently identifies the function of the enclosure, such as “electric.” Handhole enclosure covers shall require the use of tools to open, or they shall weigh over 45 kg (100 lb). Metal covers and other exposed conductive surfaces shall be bonded in accordance with 250.96(A).
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Please Post a Pic of a GROUNDED or BONDED manhole cover, I gotta see that!I;m not talking little I;m talking a 8x8x 6ft 6 or so.
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
See Article 110, Part V. for Manholes and Other Electric Enclosures Intended for Personnel Entry, All Voltages We are discussing "handholes" I could not find anything in the "manholes" reference above that would satisify your question about them.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Handholes I agree with but even thoses are going to get interesting , But All the ones I;ve seen to date have had noncontuctive covers. And if The conductors in a lot of cases are pulled right thur then what(if covers metal)??
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
While it is rarely done, 250.4(A)(3) requires the manhole cover to be bonded to provide an effective fault clearing path. Note that a large number of the manholes are owned by utilities and not subject to the NEC. Don
Don(resqcapt19)
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
Guys...sorry...I messed up the topic heading with the wording MANHOLE The topic heading was supposed to be HANDHOLE Covers. I'm interested in what is required by 2005 NEC regarding bonding of metalic handhole covers that are used on non-metalic handhole. Lets say a concrete precast base with a metalic cover used as a juction box in the ground. thanx shortcircuit
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Again!
See 314.29(D) Covers. Handhole enclosure covers shall have an identifying mark or logo that prominently identifies the function of the enclosure, such as “electric.” Handhole enclosure covers shall require the use of tools to open, or they shall weigh over 45 kg (100 lb). Metal covers and other exposed conductive surfaces shall be bonded in accordance with 250.96(A).
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
Thanx for the input guys...
So, according to Dons post, 250.4(A)(3) seems to require bonding of this metalic handhole cover used for enclosing electrical conductors...
But, according to Joes post, 250.96(A) seems to only require bonding of this metalic handhole cover if it is to serve as a grounding conductor...
Which rule do I follow?
shortcircuit
|
|
|