ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Welded Copper Connections
by gfretwell. 04/19/19 04:46 PM
Norwegian power?
by dsk. 04/19/19 10:29 AM
Israel
by annemarie1. 04/18/19 02:35 PM
Water heater calculationsSo when I count calculati
by watersparkfalls. 04/13/19 12:43 PM
Health Canada Electric Construction heaters recall
by dougwells. 04/12/19 01:22 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 11 guests, and 6 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Manhole Cover #93221
05/09/05 08:02 AM
05/09/05 08:02 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
If a non-metalic handhole has a metalic cover, is it required to be bonded according to 2005 NEC?

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Manhole Cover #93222
05/09/05 08:39 AM
05/09/05 08:39 AM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Been in a lot of them Utility and Privitely owned Have never seen one Bonded to date.

Re: Manhole Cover #93223
05/09/05 08:44 AM
05/09/05 08:44 AM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See 314.29(D) Covers. Handhole enclosure covers shall have an identifying
mark or logo that prominently identifies the function of
the enclosure, such as “electric.” Handhole enclosure covers
shall require the use of tools to open, or they shall weigh over
45 kg (100 lb). Metal covers and other exposed conductive
surfaces shall be bonded in accordance with 250.96(A).


Joe Tedesco, NEC Consultant
Re: Manhole Cover #93224
05/09/05 09:29 AM
05/09/05 09:29 AM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Please Post a Pic of a GROUNDED or BONDED manhole cover, I gotta see that!I;m not talking little I;m talking a 8x8x 6ft 6 or so.

Re: Manhole Cover #93225
05/09/05 01:11 PM
05/09/05 01:11 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See Article 110, Part V. for Manholes and Other Electric Enclosures Intended
for Personnel Entry, All Voltages

We are discussing "handholes"

I could not find anything in the "manholes" reference above that would satisify your question about them. [Linked Image]


Joe Tedesco, NEC Consultant
Re: Manhole Cover #93226
05/09/05 02:04 PM
05/09/05 02:04 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Handholes I agree with but even thoses are going to get interesting , But All the ones I;ve seen to date have had noncontuctive covers. And if The conductors in a lot of cases are pulled right thur then what(if covers metal)??

Re: Manhole Cover #93227
05/09/05 05:20 PM
05/09/05 05:20 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
While it is rarely done, 250.4(A)(3) requires the manhole cover to be bonded to provide an effective fault clearing path. Note that a large number of the manholes are owned by utilities and not subject to the NEC.
Don


Don(resqcapt19)
Re: Manhole Cover #93228
05/09/05 06:13 PM
05/09/05 06:13 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
Guys...sorry...I messed up the topic heading with the wording MANHOLE [Linked Image]

The topic heading was supposed to be HANDHOLE Covers.

I'm interested in what is required by 2005 NEC regarding bonding of metalic handhole covers that are used on non-metalic handhole.

Lets say a concrete precast base with a metalic cover used as a juction box in the ground.

thanx

shortcircuit

Re: Manhole Cover #93229
05/09/05 07:28 PM
05/09/05 07:28 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Again!

See 314.29(D) Covers. Handhole enclosure covers shall have an identifying
mark or logo that prominently identifies the function of
the enclosure, such as “electric.” Handhole enclosure covers
shall require the use of tools to open, or they shall weigh over
45 kg (100 lb). Metal covers and other exposed conductive
surfaces shall be bonded in accordance with 250.96(A).


Joe Tedesco, NEC Consultant
Re: Manhole Cover #93230
05/09/05 09:10 PM
05/09/05 09:10 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 610
massachusetts
Thanx for the input guys...

So, according to Dons post, 250.4(A)(3) seems to require bonding of this metalic handhole cover used for enclosing electrical conductors...

But, according to Joes post, 250.96(A) seems to only require bonding of this metalic handhole cover if it is to serve as a grounding conductor...

Which rule do I follow?

shortcircuit

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,459 Are you busy
190,701 Re: Forum
180,413 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.040s Queries: 15 (0.007s) Memory: 1.0229 MB (Peak: 1.1966 MB) Zlib enabled. Server Time: 2019-04-20 06:30:06 UTC