#92814 04/10/05 12:02 AM
Joined: Mar 2005
Posts: 240
Member
ok here in washington we use non isulated staples to secure romex (in minnesota we always used the insulated type) anyway people tell me you cant staple 3 14-2's under one staple. i don't see any thing on the bucket backing this statement up only its ul listing, leaving me to beleive common sense must be used. 1 14-3 and 1 14-2 are pretty darn close in thicknes which people say is ok but not 3 14-2's. any thoughts?
thanx,
h20 sparky falls

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#92815 04/10/05 12:38 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Most will have the ratings on the box. The ones I sue have one 14/3, or 12/3, or two 14/2, or 12/2. I am yet to see ones rated for three cables..... Isnt that what stackers are for?


Mark Heller
"Well - I oughta....." -Jackie Gleason
#92816 04/10/05 06:55 AM
Joined: Mar 2001
Posts: 2,056
R
Member
I'll agree with e57.
I see staples listed for (2) 14/2 or (2)12/2 but have not seen a listing for any more.
I do however regularly see 3 cables under a single staple.

BTW,
On a new residential job, I average about 150 stackers.

#92817 04/10/05 09:51 AM
Joined: Apr 2005
Posts: 15
E
Member
hi,
i have seen 4 3/12's under a 3/4 EMT strap pass inspection..

anytime i have more than two runs coming down a stud i use the 3m stackers..

3 cables under one strap doesnt look good and is a tight fit..you dont get as much penetration

brad


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The Watt Doctor
The Watt Doctor
Humble, TX
Posts: 440
Joined: December 2001
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,528 Are you busy
231,896 Re: Forum
216,531 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5