Well the students stumped me again. We were discussing 220-19 (household ranges). After going over all the notes to the tables and doing lots of examples one of them asks what to do if we have only one range but it's over 27kw. After a few minutes of searching and head scratching I had no clue. Do we just consider it 27kw? Do we continue using the "add 5% for each kw over 12" method? Or are the mfgs not permitted to make a household range over 27kw? Anybody have an answer? (preferably with refs cause I know these guys are gonna ask where I got the answer)
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
I would give the students a homework project to find a manufacturer that offers a residential range over 27KW.
Note; I have heard (I can't back it up)that large commercial cooking equipment actually states not for residential use.
Roger
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Roger: I can back that up. 2000 International Mechanical Code, section 917.2, Prohibited Locations: Cooking appliances designed, listed and labeled for use in commercial occupancies shall not be installed within dwelling units or within any area where domestic cooking operations occur.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Thank you Ryan. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) Roger
|
|
|