is it ok to use a 20 amp refridgerator circut to feed multiple receptacles please quote code thanks
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Depends on the refer..... 422.10(B) Circuits Supplying Two or More Loads. For branch circuits supplying appliance and other loads, the rating shall be determined in accordance with 210.23.
------------------------------------
210.23 Permissible Loads. In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
The requirements of 210.23 are often misunderstood. An individual (single-outlet) branch circuit can supply any load within its rating. On the other side, the load, of course, cannot be greater than the branch-circuit rating.
(A) 15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2). Exception: The small appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (2), and (3) shall supply only the receptacle outlets specified in that section.
Section 210.23(A) permits a 15- or 20-ampere branch circuit for lighting to also supply utilization equipment fastened in place, such as an air conditioner. The equipment load must not exceed 50 percent of the branch-circuit ampere rating (7.5 amperes on a 15-ampere circuit and 10 amperes on a 20-ampere circuit). However, according to 210.52(B), such fastened-in-place equipment is not permitted on the small-appliance branch circuits required in the kitchen, dining room, and so on.
(1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating. (2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures), shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied. (NEC Commentary in italics) If the refer is over 7.5A on 15A CT, or 10A on 20A CT, then it is a dedicated circuit for what-ever its rating is...... 422.10(A) Individual Circuits. The rating of an individual branch circuit shall not be less than the marked rating of the appliance or the marked rating of an appliance having combined loads as provided in 422.62. The rating of an individual branch circuit for motor-operated appliances not having a marked rating shall be in accordance with Part II of Article 430. The branch-circuit rating for an appliance that is continuously loaded, other than a motor-operated appliance, shall not be less than 125 percent of the marked rating, or not less than 100 percent of the marked rating if the branch-circuit device and its assembly are listed for continuous loading at 100 percent of its rating. Branch circuits for household cooking appliances shall be permitted to be in accordance with Table 220.19. [This message has been edited by e57 (edited 02-08-2005).]
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: Jan 2002
Posts: 163
Member
|
yes it is; there is not much to quote as the Code does not require a dedicated circuit for a refrigerator.
If you look at this in reverse: 210.52(B)(1) - says the 2 small-appliance branch circuits shall serve all the countertop receptacles required in 210.52(C)(1) AND receptacle outlets for refrigeration equipment. [Obviously the circuit load restrictions in 220 would apply].
[This message has been edited by dana1028 (edited 02-08-2005).]
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Sorry dana I was editing my post when you posted to include that.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Any which way, I usually avoid the practice. The fridge might get bigger in the future. And, nobody wants spoiled food everytime they use the toaster.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
|
Joined: Feb 2005
Posts: 3
OP
Junior Member
|
thanks guys i usualy wouldnt do it but the home owner wanted a convience recep for vac just wandered if in violation
|
|
|
|
|
Joined: Jan 2002
Posts: 163
Member
|
ditto e57 - I think it poor practice to put any other outlets/loads on the refrig. ckt.
|
|
|
|
|
Joined: Jul 2004
Posts: 10,051 Likes: 40
Member
|
New refrigerators don't really use much current. Put a clamp on one and watch it. I suppose it is still a good idea to split them out if it is easy. My 1963 house has it on the overhead light circuit and I don't see the lights dim when the fridge comes on. (new double door stainless Whirlpool fridge with all the doodads)
Greg Fretwell
|
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
New refrigerators don't really use much current. I agree, my fridge is medium sized and is labeled at 4.75 amps @ 115 volts. Many other items in my kitchen are more of a concern. My microwve 1800 watts @ 120 volts. (15 amps) My 'Hot Shot' (It boils water for one cup of coffee) 1475 watts. Small convection oven 1800 watts. All of those are counter top appliances that run from the small appliance branch circuits. [This message has been edited by iwire (edited 02-11-2005).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
|
Joined: Dec 2004
Posts: 329
Member
|
You mentioned that the HO wanted a convenience recept for a VAC. I'm assuming that you were referring to a vacuum cleaner, I would probably advise the HO against it. My reasoning is while new fridges have a lower draw than in the past vacuum cleaners still tend to draw a fair amount of juice. The draw of the vac and the staring current of the fridge could possibly trip the breaker. Perhaps I may be being to cautious, but after the last hurricane season down here in FLA, I know first hand how much a fridge full of spoiled food sucks. Just my $.02 Ian
[This message has been edited by IanR (edited 02-11-2005).]
|
|
|
Posts: 30