Residential receptacle spacing #91703
01/31/05 04:41 PM
01/31/05 04:41 PM
E
earlydean  Offline OP
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Does a duplex receptacle still count for general lighting receptacles per 210.52(A)(within 6 feet of any spot on the wall) if the receptacle is switched (both halves)as allowed by 210.70(A)(1)exc.1? Or, is it required to split the duplex receptacle into one outlet always hot and the other switched?


Earl
2017 / 2014 NEC & Related Books and Study Guides
Re: Residential receptacle spacing #91704
01/31/05 06:53 PM
01/31/05 06:53 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,373
Estero,Fl,usa
Looks legal to me, although perhaps a bad design


Greg Fretwell
Re: Residential receptacle spacing #91705
01/31/05 07:30 PM
01/31/05 07:30 PM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
I don't recall the Code excluding switched receptacles... it just says that they have to be the minimum distance (12') apart, or 6' from any point along a wall.

Nothing about always hot.

Re: Residential receptacle spacing #91706
02/01/05 06:03 AM
02/01/05 06:03 AM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
If you switch the top and bottom of a duplex receptacle, it becomes a lighting outlet and would not meet the requirements on spacing for receptacle outlets as specified in 210.52(A)(1)

So...common practice is to switch half of the receptacle outlet in a room to meet the requirements of both 210.52(A)(1) and 210.70(A)(1)

It is not required to be split,but if you don't you must also locate a "Live" receptacle outlet next to the switched lighting outlet to meet the spacing requirements.

My practice is to switch the top half so when the homeowner plugs in a cordless phone with those little square power transformers it does not cover the other half of the receptacle.

shortcircuit

Re: Residential receptacle spacing #91707
02/01/05 09:14 AM
02/01/05 09:14 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
shortcircuit,
Quote
If you switch the top and bottom of a duplex receptacle, it becomes a lighting outlet and would not meet the requirements on spacing for receptacle outlets as specified in 210.52(A)(1)

Please cite the code section that says this. Thanks.


Don(resqcapt19)
Re: Residential receptacle spacing #91708
02/01/05 09:39 AM
02/01/05 09:39 AM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
Short Circuit

That is a Mass Amendment!


Charlie

Re: Residential receptacle spacing #91709
02/01/05 10:04 AM
02/01/05 10:04 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,498
Michigan USA
Don- I believe that's called a "vest pocket" rule" [Linked Image] Also, I think DougW meant to say "maximum" in stead of "Minimum 12 feet." in his comment.


George Little
Re: Residential receptacle spacing #91710
02/01/05 11:48 AM
02/01/05 11:48 AM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
George
Please explain "vest pocket"??

Charlie

Re: Residential receptacle spacing #91711
02/01/05 02:04 PM
02/01/05 02:04 PM
I
IanR  Offline
Member
Joined: Dec 2004
Posts: 328
Palm Bay FL USA
quote:
--------------------------------------------------------------------------------
If you switch the top and bottom of a duplex receptacle, it becomes a lighting outlet and would not meet the requirements on spacing for receptacle outlets as specified in 210.52(A)(1)
--------------------------------------------------------------------------------

I don't think that is an NEC requirement. Down here in Central FLA none of the outlets I have seen are split switched, the room light switch operates the whole duplex.
Ian

Re: Residential receptacle spacing #91712
02/01/05 03:20 PM
02/01/05 03:20 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,373
Estero,Fl,usa
Ian, I suppose it is just regional, even when we are on exactly the same code. In Lee County Fl. they want "half hots" but I doubt they actually check close enough to catch folks 99.999% of the time.
Inspectors are so overworked around here I wonder how they find anything.
(30 or more a day)
A agree there is no clear code language to enforce it.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,162 Are you busy
192,980 Re: Forum
182,639 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.006s) Memory: 1.0246 MB (Peak: 1.2016 MB) Zlib enabled. Server Time: 2019-07-21 21:50:20 UTC