I just have 2 quick questions
can I have line and load in the same raceway?
and what is derating?

thank you

2017 / 2014 NEC & Related Books and Study Guides
Joined: Mar 2003
Posts: 849
Y
Member
I;d say yes and derateing by 310.15(B)2

Joined: Dec 2003
Posts: 751
E
Member
Line and load is OK in the same raceway, but service and feeder, or service and branch circuit conductors cannot be in the same raceway.
De-rating is contained in the bottom section of Table 310.16 for ambient temperature, and in Table 310.15(B)(2)(a) for more than 3 current carrying conductors in a raceway or cable, or bundling of cables


Earl

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The Watt Doctor
The Watt Doctor
Mont Belvieu, TX
Posts: 437
Joined: December 2001
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,448 Are you busy
213,527 Re: Forum
200,406 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5