#91700 01/31/05 01:11 PM
Joined: Jun 2004
Posts: 6
R
Junior Member
Hi
I just have 2 quick questions
can I have line and load in the same raceway?
and what is derating?

thank you

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2003
Posts: 849
Y
Member
I;d say yes and derateing by 310.15(B)2

Joined: Dec 2003
Posts: 751
E
Member
Line and load is OK in the same raceway, but service and feeder, or service and branch circuit conductors cannot be in the same raceway.
De-rating is contained in the bottom section of Table 310.16 for ambient temperature, and in Table 310.15(B)(2)(a) for more than 3 current carrying conductors in a raceway or cable, or bundling of cables