Good morning Don,
I don’t have a copy of the NEC in front of me but in my opinion if the underground water pipe is not part of the structure with the service you don’t have to use it. If the separate building has a metal underground pipe it should be used as part of the grounding electrode system of that building and connected to the EGC in the service disconnect for that building.
Curt
Curt Swartz
Work Gear for Electricians and the Trades
Workgear for Electricians
#91645 01/31/05 12:34 PM
Curt,
I could be wrong, but I don't think we are talking about a second building in the original post. Look at the second post by the original poster.
Don
Don(resqcapt19)
#91646 01/31/05 09:14 PM
Ya, It's only 1 building.
Yes we were in Northbrook at the class the other day. I dinn't expect someone elce from here would show up.
Tom
#91647 01/31/05 09:38 PM
Tom
Is the meter/main attached to the dwelling?
Curt
Curt Swartz
#91648 01/31/05 10:10 PM
Yes, it's attached to the dwelling.
#91649 01/31/05 10:38 PM
When you said pedestal I was picturing the meter/main mounted remote from the dwelling. Somehow even though Don told me to look at your second post I missed it but saw it after making my last reply. I’m having one of those days.
Curt