Meter Main Bonding #91634 01/27/05 11:16 PM
Joined: Feb 2003
Posts: 687
A
Active 1 Offline OP
Member
We have a 200 amp meter pedistal with a built in 200 amp circuit breaker. About 35' feet away is the first 200 amp panel. An equipment ground is run from the pedistal to the 200 amp panel with the 3 3ott conductors.

The dispute is if the 200 a panel inside should have the main bond screw in (bonding the neutral to ground).

I believe the meter serves as the main disco and is by design bonding the nutral and equipment ground. The inside panel would not be a service panel because the meter is the service. Right?

Then the water pipe ground should go to the meter and not the panel?

Thanks,

Tom

2017 / 2014 NEC & Related Books and Study Guides
Re: Meter Main Bonding #91635 01/28/05 12:00 AM
Joined: Jul 2004
Posts: 9,543
G
gfretwell Offline
Member
If you are running 4 wires you will not reground the neutral at the second panel. That creates a parallel path.


Greg Fretwell
Re: Meter Main Bonding #91636 01/28/05 06:05 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
I agree, you would not tie the two together in these downstream panels.

Now, whether or not a ground rod is necessary at the down stream panels would be found in 250.32. [Linked Image]

Roger

Re: Meter Main Bonding #91637 01/28/05 08:07 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
I'd say ground rod or rods at meter base (install bonding screw), 4 wires from meter base to panel at the house. Float neutral bar at the house, Tie water pipe and what every gounding you have to the ground bar at the house.This is simlar to a Trailer hookup . If disconnect was mounted on the house outside then I;d say grounds to to panel outside, when remote I;d say No.

Re: Meter Main Bonding #91638 01/28/05 09:44 PM
Joined: Feb 2001
Posts: 308
S
Steve T Offline
Member
You have it correct.

Now the next question is--can the GEC pass through the panel? (No splice)

Re: Meter Main Bonding #91639 01/29/05 06:04 PM
Joined: May 2004
Posts: 162
C
cpal Offline
Member
What is the breaker on the pedistal used for ??

Hot sequence or cold??

Just a thought

Charlie

Re: Meter Main Bonding #91640 01/30/05 03:31 PM
Joined: Feb 2003
Posts: 687
A
Active 1 Offline OP
Member
The disconect meter pedistal is mounted on the side of the house. Thanks for yor replys.


Tom

Re: Meter Main Bonding #91641 01/31/05 12:03 AM
Joined: Mar 2004
Posts: 55
E
eswets Offline
Member
Tom,
I had a job like that. 200amp breaker on the meter ped, 200amp mlo panel. 2" ridgid from meter to panel with out bond screw. 3/4" conduit from meter to cold water ground. Thats how inspector wanted it.
BTW were you at leviton's LIN class in Northbrook on thursday? though I saw your company name.

Re: Meter Main Bonding #91642 01/31/05 01:21 AM
Joined: Apr 2002
Posts: 558
C
caselec Offline
Member
The water piping of the dwelling should be bonded to the EGC buss of the panel at the dwelling. It should not be run separately to the meter main.

Curt


Curt Swartz
Re: Meter Main Bonding #91643 01/31/05 08:09 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Curt,
If there is metal underground water pipe, then the conductor between the water pipe and the electrical system is a grounding electrode conductor and must be connected to the grounded conductor at or on the line side of the service disconenct per 250.24(A)(1).
Don


Don(resqcapt19)
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,057 Are you busy
205,954 Re: Forum
194,003 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3