main breaker #91519 01/20/05 07:23 PM
Joined: Jan 2005
Posts: 71
S
sid123456 Offline OP
Member
where does it say that the main breaker has to be at the meter if the panel is so far away? i can't seem to find this.

2017 / 2014 NEC & Related Books and Study Guides
Re: main breaker #91520 01/20/05 07:29 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Sid, the closest you'll get is 230.70(A)(1).

This pretty much leaves it up to the AHJ and local requirements.

Roger

Re: main breaker #91521 01/20/05 08:13 PM
Joined: Jan 2005
Posts: 71
S
sid123456 Offline OP
Member
maybe its local code...

Re: main breaker #91522 01/20/05 08:17 PM
Joined: Jan 2005
Posts: 71
S
sid123456 Offline OP
Member
they say (some people) if its back to back you can put your main in the panel....

Re: main breaker #91523 01/20/05 08:31 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Sid, have you read 230.70(A)(1)?

Roger

Re: main breaker #91524 01/20/05 08:35 PM
Joined: Jan 2005
Posts: 71
S
sid123456 Offline OP
Member
yes, its not very specific. nearest point.... then 30 or 50 feet from the meter would be fine.. right? or is nearest point always the meter? those meter mains are 100 buck plus the mlo is 100 too. just trying to save a 100

Re: main breaker #91525 01/20/05 08:58 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Sid,
Quote
they say (some people) if its back to back you can put your main in the panel....
they are right, this meets the requirement of 230.70(A)(1).

This can be as much as 5,6, or even 10' in some locations. I don't know of any where that would allow 50', however you might want to look at 230.6 if you must run this far.

Roger

Re: main breaker #91526 01/20/05 09:00 PM
Joined: Jan 2005
Posts: 71
S
sid123456 Offline OP
Member
thanks roger


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,207 Are you busy
206,095 Re: Forum
194,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3