Posted By: sid123456 main breaker - 01/21/05 12:23 AM
where does it say that the main breaker has to be at the meter if the panel is so far away? i can't seem to find this.
Posted By: Roger Re: main breaker - 01/21/05 12:29 AM
Sid, the closest you'll get is 230.70(A)(1).

This pretty much leaves it up to the AHJ and local requirements.

Roger
Posted By: sid123456 Re: main breaker - 01/21/05 01:13 AM
maybe its local code...
Posted By: sid123456 Re: main breaker - 01/21/05 01:17 AM
they say (some people) if its back to back you can put your main in the panel....
Posted By: Roger Re: main breaker - 01/21/05 01:31 AM
Sid, have you read 230.70(A)(1)?

Roger
Posted By: sid123456 Re: main breaker - 01/21/05 01:35 AM
yes, its not very specific. nearest point.... then 30 or 50 feet from the meter would be fine.. right? or is nearest point always the meter? those meter mains are 100 buck plus the mlo is 100 too. just trying to save a 100
Posted By: Roger Re: main breaker - 01/21/05 01:58 AM
Sid,
Quote
they say (some people) if its back to back you can put your main in the panel....
they are right, this meets the requirement of 230.70(A)(1).

This can be as much as 5,6, or even 10' in some locations. I don't know of any where that would allow 50', however you might want to look at 230.6 if you must run this far.

Roger
Posted By: sid123456 Re: main breaker - 01/21/05 02:00 AM
thanks roger