#91378 01/13/05 02:17 PM
Joined: Mar 2004
Posts: 49
T
Member
IS IT acsecptable for the power company service line to run over liveable dwelling?If it is how far off the roof does it need to be?

Work Gear for Electricians and the Trades

Workgear for Electricians

#91379 01/13/05 02:23 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Yes, 230.24(A)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#91380 01/28/05 02:58 PM
Joined: Jan 2005
Posts: 5
D
Junior Member
it is acceptable so long as the point of attachment sustains a 3' clearance above roof for the roofers sake

#91381 01/28/05 03:52 PM
Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
That 3' is only "final conductor span" leading to the service head. Normally the clearance is 8' above the roof for a distance of 3' beyond the roof edge.


Greg Fretwell
#91382 01/29/05 02:02 PM
Joined: Apr 2004
Posts: 201
Member
Actually, the NESC is the Code that covers the serving electric utility’s service drop clearances. The 3 ft beyond the roof’s edge is not in the NESC. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
#91383 01/29/05 10:24 PM
Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
What is the NESC rule for height over a roof?


Greg Fretwell
#91384 01/29/05 11:19 PM
Joined: Mar 2004
Posts: 829
B
Member
It's up to the POCO. Here they won't allow the eight foot riser if it's more than 3 feet from the edge because they don't allow the line crews to use a ladder on the roof for safety reasons. So they specify five feet, no matter how much of the drop extends over the roof.

Work Gear for Electricians and the Trades

Workgear for Electricians

#91385 01/30/05 10:23 PM
Joined: Oct 2000
Posts: 3,672
Likes: 5
Administrator
Member
Quote
These are "before and after" photos of one result of a service change I did. As you can see, the service drop has a lot more clearance than it previously had.

So, yes, you can run these conductors over a dwelling, but you do need 36" clearance. While I believe that this is covered in NEC 230-24, your local utility is likely to have a different rule.

- renosteinke
[Linked Image]

#91386 01/30/05 10:39 PM
Joined: Jul 2004
Posts: 10,051
Likes: 40
G
Member
If this drop is not going to the building in question I think 230.24 says it has to be 8 feet above the roof, out to a distance of 3 feet from the roof's edge. The exception (4) is for the final span of the drop that connects to the riser on the building served


Greg Fretwell
#91387 02/01/05 09:37 PM
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
Somehow the "before" and "after shots got reversed [Linked Image]. I hate it when that happens!
I will admit that 230 also references the pitch of the roof; this roof is right on the line, and I let the inspector decide. Part of this was based upon the heigth of the riser on the building getting new service; see photos added to "flagpoles" in "photos submitted for discussion."