I am looking at the side of a 20 amp Square D breaker type HOM series 1 and it shows a pictorial of two # 14 load wires under the screw/pressure plate.
I see two issues,first the # 14 on a 20 amp breaker and 2 load wires on a single pole breaker.
Does SQ D assume that the load is split evenly ?
How can they show this as acceptable?
I have called Square D and they are researching it.
Chris (having a senior moment)

Work Gear for Electricians and the Trades
Re: Square D HOM SP breaker #9108
04/17/02 10:55 AM
04/17/02 10:55 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I believe the purpose of diagram you are looking at is only to show that this type of breaker has terminals that can accomodate 2 conductors of equal size. I don't have one in front of me, but I think it also lists acceptable wire sizes. It is unfortunate that they chose #14 to illustrate the fact that the terminals accept 2 conductors, but it is up tp the installer to properly size the circuit conductors.

Re: Square D HOM SP breaker #9109
04/18/02 08:52 AM
04/18/02 08:52 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
They are showing the range of the lug not the range of the breaker. They use the same lug on all breakers from 15 to 30 Amps. It is up to the installer to chose the correct wire for the application. Remember not all #14 AWG wiring is restricted to 15 amp protection (i.e. motors).


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
253,279 Are you busy
189,904 Re: Forum
179,619 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9504 MB (Peak: 1.0758 MB) Zlib enabled. Server Time: 2019-02-21 13:56:49 UTC