ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Any Woodworkers here?
by gfretwell - 05/13/21 01:47 AM
Your favourite food?
by Bill Addiss - 05/12/21 05:23 PM
Lock-down Thread
by gfretwell - 05/11/21 12:30 PM
Do You Travel?
by gfretwell - 05/11/21 12:16 PM
Just be aware of this...
by gfretwell - 05/10/21 07:30 PM
New in the Gallery:
2020 - 2021 Winter Project
Garden 2021
Who's Online Now
0 registered members (), 17 guests, and 23 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Square D HOM SP breaker #9107 04/17/02 10:40 AM
Joined: May 2001
Posts: 160
C
Chris Rudolph Offline OP
Member
I am looking at the side of a 20 amp Square D breaker type HOM series 1 and it shows a pictorial of two # 14 load wires under the screw/pressure plate.
I see two issues,first the # 14 on a 20 amp breaker and 2 load wires on a single pole breaker.
Does SQ D assume that the load is split evenly ?
How can they show this as acceptable?
I have called Square D and they are researching it.
Chris (having a senior moment)

Work Gear for Electricians and the Trades
Re: Square D HOM SP breaker #9108 04/17/02 11:55 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
I believe the purpose of diagram you are looking at is only to show that this type of breaker has terminals that can accomodate 2 conductors of equal size. I don't have one in front of me, but I think it also lists acceptable wire sizes. It is unfortunate that they chose #14 to illustrate the fact that the terminals accept 2 conductors, but it is up tp the installer to properly size the circuit conductors.

Re: Square D HOM SP breaker #9109 04/18/02 09:52 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
They are showing the range of the lug not the range of the breaker. They use the same lug on all breakers from 15 to 30 Amps. It is up to the installer to chose the correct wire for the application. Remember not all #14 AWG wiring is restricted to 15 amp protection (i.e. motors).


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Admin 11
Popular Topics(Views)
278,942 Are you busy
212,092 Re: Forum
199,115 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3