Conductors from different panels using same conduit #90751 12/09/04 08:28 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
I have a job that I am to wire a dedicated circuit to. I can use a conduit that is in the same area, but the panel is full. There is another panel beside it, that is not full. The easiest way I see, is use the conduit, and set a juncion box at the panel location, and pipe into the other panel. Is this acceptacle to code? I found it in the 99 code, but can't seem to find it in the new code. Thanks for the help. Steve...

p.s I was looking in the wrong section of the new code [Linked Image] my mistake again. The best I read in 300-3 (c) that circuits rated 600 volts or less can be run in the same raceway, etc....

[This message has been edited by sparkync (edited 12-09-2004).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Conductors from different panels using same conduit #90752 12/09/04 11:51 AM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
This is what you are looking for.
312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.


Greg Fretwell
Re: Conductors from different panels using same conduit #90753 12/09/04 12:06 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Steve another area that specifically rcognizes and allows this would be 200.6(D), this is allowing different systems which would definately be from two different panels.

Roger

Re: Conductors from different panels using same conduit #90754 12/09/04 12:32 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Thanks for the replies. Steve...


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,880 Are you busy
205,739 Re: Forum
193,850 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3