0 members (), 973 guests, and 8 robots.
#90428 11/21/04 12:40 AM
We have 3 3 phase 3 HP fan motors that are
continuous duty.
Can we use cord and plug and the breaker
to operate the motors? or do we have to
use a overload section on each motor?
Thanks,
Sparky_1
Workgear for Electricians
#90429 11/21/04 10:03 AM
Tom Offline
Most 3 phase motors do not have built in overload protection. You have to install an overload device in each conductor & this is usually done with a motor starter. See 430.32
As for using the cord & plug connection, that will require a horsepower rated receptacle and a horsepower rated cord cap.430.109(F)
#90430 11/21/04 10:51 AM
Thanks for the information Tom