#90428 11/21/04 01:40 AM
Joined: Nov 2004
Posts: 14
S
Member
We have 3 3 phase 3 HP fan motors that are
continuous duty.
Can we use cord and plug and the breaker
to operate the motors? or do we have to
use a overload section on each motor?

Thanks,
Sparky_1

2017 / 2014 NEC & Related Books and Study Guides
#90429 11/21/04 11:03 AM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Most 3 phase motors do not have built in overload protection. You have to install an overload device in each conductor & this is usually done with a motor starter. See 430.32

As for using the cord & plug connection, that will require a horsepower rated receptacle and a horsepower rated cord cap.430.109(F)

Tom


Few things are harder to put up with than the annoyance of a good example.
#90430 11/21/04 11:51 AM
Joined: Nov 2004
Posts: 14
S
Member
Thanks for the information Tom


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
Admin 10
Popular Topics(Views)
280,481 Are you busy
213,569 Re: Forum
200,439 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5