From the Suncoast Division of the IAEI It is a very common practice around here to have a blank cover for the lighting outlet, even on a $800,000 house. Question: Is an electrical inspector correct for asking that a lighting fixture (or lampholder) be installed at lighting outlets where they exist instead of a blank cover, such as in a kitchen or bathroom, or in any other location before allowing occupancy?
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
In a kitchen or bathroom I think a light must be installed in order to satisfy 210.70, although I can see where a person could argue it.
If the light is in a location where a lighting outlet is not required, then I would have to allow a blank cover.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
It is clear all that is required by the NEC is an outlet. 210.70 Lighting Outlets Required.
Lighting outlets shall be installed where specified in 210.70(A), (B), and (C).
(A) Dwelling Units. In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (2), and (3).
(1) Habitable Rooms. At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Outlet. A point on the wiring system at which current is taken to supply utilization equipment. Perhaps there are building codes that actually require illumination. You can only enforce what the code states, especially true when the words are in article 100 [This message has been edited by iwire (edited 10-31-2004).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: May 2004
Posts: 697
Member
|
Although it's as tacky as it can be, I agree that by definition, the outlet is required, but the utilization equiptment (the light in this case)isn't. Having argued the technicality of the NEC, I'd always install a light, even if only an open-bulb plastic light (75 cents?). I wouldn't want to loose a customer over a few dollars.
Dave
|
|
|
|
Joined: Feb 2002
Posts: 375
Member
|
I believe that the intent of the code is to provide lighting without requiring an additional permit to install the fixtures.
While only an outlet, the recepticle, is required at a recepticle, a fixture is required at a juction box.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Forgetting about what each of us would do, or what the NFPAs intent is, what does 210.70 state? Article 100 Lighting Outlet. An outlet intended for the direct connection of a lampholder, a luminaire (lighting fixture), or a pendant cord terminating in a lampholder. Notice it states "intended", it does not state "equipped with" The 2002 NEC use the word Luminaire over 250 times, why not here in 210.70? The exception that allows "receptacles controlled by a wall switch" specifically states receptacles, not receptacle outlets. Still we are not required to leave a floor lamp. Tacky or not that is how I see it. I am interested in how this can be interpreted any other way? Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2002
Posts: 375
Member
|
Outlet: A point on the wiring system at which current is taken to supply utilization equipment.
It can be argued that the phrase "IS TAKEN" requires a fixture as well as bulbs to transform the junction box into an outlet.
But I can see where people might want to select their own lighting fixtures and I would not object to that either.
|
|
|
|
Joined: Jul 2004
Posts: 9,988 Likes: 35
Member
|
George, are you saying you would fail a final if there was a burned out bulb?
Greg Fretwell
|
|
|
|
Anonymous
Unregistered
|
It's pretty common in the Denver area as well. Here is the scenario: Family room,(Or other room)has switched receptacle to meet the intent of the code. Then a switch and lighting opening are roughed in for a ceiling fan and it is an option to either hang a builder furnished fan at the time the home is built or have a blank installed for installation at a later point. In this situation I would rather see a blank plate than a keyless.
|
|
|
|
Joined: Apr 2002
Posts: 178
Member
|
Well I can see both sides of this one.We regularly have a blank where additional fans lights maybe installed at home owners leisure.But in most cases there`s some source of lighting to meet code.Because they won`t pass off on blank cover say in kitchen.Sometimes we get by with the over sink light.I mean everyone knows a nice light will be installed but I guess is it installed properly and by whom could be the question
|
|
|
Posts: 440
Joined: December 2001
|
|
|
|