Ran across this setup the other day: From house panel to GFCI disconnect using 6/2 UF and an individual #6 THWN conductor. In the UF, the two #6 are wired as hot, the bare #10 is the neutral, and the individual THWN is the ground. Is there any reason for doing it this way or is this just sloppy work by a "licensed" electrician?
|
|
|
|
Joined: Feb 2004
Posts: 494
Member
|
hi, the installation you described does not meet the code..first..all conductors of the circuit must be in the same cable or raceway..there are more rules that apply here than you have mentioned..what type of wire/cable is feeding the disconnect? inside wiring method can not be used for exterior wiring..you must transition from romex to an approved method..like thhn in a raceway or something else..
there are folks out there with more to say on this i am sure..
sounds like no planning to me..and no experience dealing with this type of installation..
nice try but no dice..
-regards
mustang
[This message has been edited by mustangelectric (edited 10-26-2004).]
|
|
|
|
Joined: Apr 2001
Posts: 518
Member
|
I can't say I've seen UF with a downsized third wire... #6 seems large for most hot tubs- is voltage drop an issue?... I can't see anybody with real electrical training doing this!
|
|
|
|
Joined: Oct 2004
Posts: 9
OP
Junior Member
|
It's a 50A feed to the 50A GFCI disconnect so #6 is required. I too think it is an improper setup, but the HO swears by the reputation and experience of the electrician who installed it. My guess is he added the separate wire after the UF was in place once he realized he was a wire short.
|
|
|
|
Joined: Nov 2003
Posts: 269
Member
|
I see violations of 300.3(A),300.3(B),and 340.108. 6AWG UF or NM will have a 10AWG EGC (250.122)
John
|
|
|
|
Joined: May 2004
Posts: 697
Member
|
IMO the homeowner can swear all he wants, it's sloppy work.