Spa wiring #89985 10/26/04 10:05 PM
Joined: Oct 2004
Posts: 9
N
normel Offline OP
Junior Member
Ran across this setup the other day:
From house panel to GFCI disconnect using 6/2 UF and an individual #6 THWN conductor. In the UF, the two #6 are wired as hot, the bare #10 is the neutral, and the individual THWN is the ground.
Is there any reason for doing it this way or is this just sloppy work by a "licensed" electrician?

2017 / 2014 NEC & Related Books and Study Guides
Re: Spa wiring #89986 10/26/04 10:10 PM
Joined: Feb 2004
Posts: 494
M
mustangelectric Offline
Member
hi,
the installation you described does not meet the code..first..all conductors of the circuit must be in the same cable or raceway..there are more rules that apply here than you have mentioned..what type of wire/cable is feeding the disconnect? inside wiring method can not be used for exterior wiring..you must transition from romex to an approved method..like thhn in a raceway or something else..

there are folks out there with more to say on this i am sure..

sounds like no planning to me..and no experience dealing with this type of installation..

nice try but no dice..

-regards

mustang

[This message has been edited by mustangelectric (edited 10-26-2004).]

Re: Spa wiring #89987 10/26/04 10:33 PM
Joined: Apr 2001
Posts: 518
J
John Steinke Offline
Member
I can't say I've seen UF with a downsized third wire... #6 seems large for most hot tubs- is voltage drop an issue?... I can't see anybody with real electrical training doing this!

Re: Spa wiring #89988 10/27/04 07:11 AM
Joined: Oct 2004
Posts: 9
N
normel Offline OP
Junior Member
It's a 50A feed to the 50A GFCI disconnect so #6 is required. I too think it is an improper setup, but the HO swears by the reputation and experience of the electrician who installed it. My guess is he added the separate wire after the UF was in place once he realized he was a wire short.

Re: Spa wiring #89989 10/27/04 11:34 AM
Joined: Nov 2003
Posts: 269
E
electricman2 Offline
Member
I see violations of 300.3(A),300.3(B),and 340.108. 6AWG UF or NM will have a 10AWG EGC (250.122)


John
Re: Spa wiring #89990 10/27/04 03:18 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
IMO the homeowner can swear all he wants, it's sloppy work.

Dave


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,948 Are you busy
205,833 Re: Forum
193,912 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3