#89985 10/26/04 11:05 PM
Joined: Oct 2004
Posts: 9
N
normel Offline OP
Junior Member
Ran across this setup the other day:
From house panel to GFCI disconnect using 6/2 UF and an individual #6 THWN conductor. In the UF, the two #6 are wired as hot, the bare #10 is the neutral, and the individual THWN is the ground.
Is there any reason for doing it this way or is this just sloppy work by a "licensed" electrician?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#89986 10/26/04 11:10 PM
Joined: Feb 2004
Posts: 494
M
Member
hi,
the installation you described does not meet the code..first..all conductors of the circuit must be in the same cable or raceway..there are more rules that apply here than you have mentioned..what type of wire/cable is feeding the disconnect? inside wiring method can not be used for exterior wiring..you must transition from romex to an approved method..like thhn in a raceway or something else..

there are folks out there with more to say on this i am sure..

sounds like no planning to me..and no experience dealing with this type of installation..

nice try but no dice..

-regards

mustang

[This message has been edited by mustangelectric (edited 10-26-2004).]

#89987 10/26/04 11:33 PM
Joined: Apr 2001
Posts: 518
J
Member
I can't say I've seen UF with a downsized third wire... #6 seems large for most hot tubs- is voltage drop an issue?... I can't see anybody with real electrical training doing this!

#89988 10/27/04 08:11 AM
Joined: Oct 2004
Posts: 9
N
normel Offline OP
Junior Member
It's a 50A feed to the 50A GFCI disconnect so #6 is required. I too think it is an improper setup, but the HO swears by the reputation and experience of the electrician who installed it. My guess is he added the separate wire after the UF was in place once he realized he was a wire short.

#89989 10/27/04 12:34 PM
Joined: Nov 2003
Posts: 269
E
Member
I see violations of 300.3(A),300.3(B),and 340.108. 6AWG UF or NM will have a 10AWG EGC (250.122)


John
#89990 10/27/04 04:18 PM
Joined: May 2004
Posts: 697
D
Member
IMO the homeowner can swear all he wants, it's sloppy work.

Dave