fire pump controller #8989
04/12/02 01:16 AM
04/12/02 01:16 AM
C
Cindy  Offline OP
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
i dont do fire pumps every day, hope i dont sound too stupid asking,
whatever, this is a loooong question

i'm a little confused by a one-line diagram on some plans. it shows 2 sources, the mdp and mde supplying emgcy power, to the fire pump controller. from there one circuit goes to the fire pump and the other goes to the jockey pump controller.
but the fire pump controller has a warning note that refers to nfpa20 7-3.4.4, same as 695.1, that says the fire pump controller cant be used as a j-box to supply other equipment, (assuming they are referring to the jockey pump).
it also says the supply for the jockey pump controller cant be connected to the fire pump controller. but i think the one-line showed both the fire and jockey pumps coming from the fire pump controller.
then if thats not enough confusion we dont show the 480v 100a 3ph transfer switch in the one-line but it is supposed to be located just ahead of the fire pump controller with sources from the mdp and mde using a generator for backup power.

all of that said, isnt it just saying to keep the jockey pump controller and fire pump controller separated? and if so then the one-line shouldnt show the jockey pump coming from the fire pump controller, right?

i think i remember reading that jockey pumps are ok on the fire pump feeders though, which seems to contradict what nfpa20 says?

695.4 says for power continuity when making a direct connection using a transfer switch that it should be listed as a combination fire pump controller and power transfer switch, or, a by making a supervised connection of the disco and ocpd between the source and the listed [fpc] fire pump controller and [pts] power transfer switch combination.

so does that mean that if you use a transfer switch that you have to use a listed combination fpc/pts?

dont worry, someone will help me with this, but you guys offer valuable perspectives, so thot i'd at least ask.

Work Gear for Electricians and the Trades
Re: fire pump controller #8990
04/12/02 11:40 AM
04/12/02 11:40 AM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
OK Cindy.....I can trump your "stupid" question. [Linked Image]

What is a jockey pump??

GJ

Re: fire pump controller #8991
04/12/02 11:43 AM
04/12/02 11:43 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Are MDP and MDE service drops, or ditribution boards, or what? There are specific requirements for the acceptable types of sources of a fire pump.
No matter the configuration of the two sources, they have to be transfered by a transfer switch listed for fire pump service. Most controllers can be ordered with an appropriate trans. switch upstream in the same enclosure.
If you have the code handbook, they have good diagrams of the distribution schemes.


Ron
Re: fire pump controller #8992
04/12/02 11:45 AM
04/12/02 11:45 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
A Jockey pump is a booster pump that keeps the pressure up, without having to run the larger, more inefficient fire pump.

[This message has been edited by Ron (edited 04-12-2002).]


Ron
Re: fire pump controller #8993
04/12/02 07:32 PM
04/12/02 07:32 PM
G
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
Cindy,

Great topic here!

We just picked up a nursing home project that will be built over the next 12 months. This will be my first project with a fire pump install so I'm interested in anything that you learn.

GJ

Re: fire pump controller #8994
04/13/02 06:23 PM
04/13/02 06:23 PM
N
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
If you study artice 695 with the idea that the fire pump is to run no matter what, you will understand those poorly drawn diagrams.
You can tap the fire pump conductors ahead of the fire pump controller to power the jockey pump. Any thing else (ie lights and outlets) in the pump/sprinker room is served from a different source.
We have always had several inspectors looking at fire pump install- at least one will want something not on the drawings.
recomend you look at NFPA 20 before you start work.

good luck


ed

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 9
Popular Topics(Views)
249,439 Are you busy
187,355 Re: Forum
176,696 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.9770 MB (Peak: 1.1180 MB) Zlib enabled. Server Time: 2018-09-24 23:46:33 UTC