Hi,
Is there ever a time where a MAIN PANELBOARD for a Sinfgle Fam Dwelling would NOT have a #4 bare ground for cold water ground? copper piping.

here in Arkansas the GEC goes from the Ground rod to the METER BASE. In Kentucky it is from the Panelboard to the Ground Rod. If there is a copper water line, you need a COLD WATER BOND..usually a #6 for 100A and #4 for 200A this ALWAYS goes to the MAIN PANELBOARD..

i saw a house today that only had a gec from the main disc at the meter..no other ground in the panel..

this looked wrong to me..

the feed was a 4 conductor SER type cable..

thanks for any replies..

mustang

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

#89327 09/09/04 09:51 PM
Joined: May 2004
Posts: 697
D
Member
Allways check with the AHJ.

Dave

#89328 09/09/04 10:15 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
GEC's are required to go from the electrode to the service equipment. If the disco at the meter is the service equipment, and it sounds like it is, this is code compliant.


Ryan Jackson,
Salt Lake City
#89329 09/09/04 11:21 PM
Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
It can be anywhere from the load end of the drop to the disconnect enclosure.

250.24 Grounding Service-Supplied Alternating-Current Systems.
(A)(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.


Greg Fretwell
#89330 09/10/04 10:34 PM
Joined: Feb 2002
Posts: 2,233
H
Member
What if all of the water piping in the house is PLASTIC? What do you ground to?


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,347 Are you busy
231,744 Re: Forum
216,374 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5