#89072 08/27/04 11:26 PM
Joined: Dec 2002
Posts: 13
M
Member
I am wiring an office that has a suspended ceiling that serves as a return air space above it. Code book says I can use ent above suspended ceilings if it is fire rated at 15 minutes. It doesn't say I can't use it either in this situation. In the Nec it does say that ent is flame retardent. Can I use it? What is your opinion.

2017 / 2014 NEC & Related Books and Study Guides
#89073 08/27/04 11:27 PM
Joined: Dec 2003
Posts: 886
H
Member
No.

-Hal

#89074 08/28/04 10:16 AM
Joined: Jun 2004
Posts: 220
T
Member
300-21(c)1.no ENT

#89075 08/28/04 10:19 PM
Joined: Dec 2002
Posts: 13
M
Member
Thanks guys, I missed that in the code book.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Top Posters(30 Days)
Admin 10
Popular Topics(Views)
280,476 Are you busy
213,562 Re: Forum
200,434 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5