Posted By: master44 ENT is it plenum rated. - 08/28/04 03:26 AM
I am wiring an office that has a suspended ceiling that serves as a return air space above it. Code book says I can use ent above suspended ceilings if it is fire rated at 15 minutes. It doesn't say I can't use it either in this situation. In the Nec it does say that ent is flame retardent. Can I use it? What is your opinion.
Posted By: hbiss Re: ENT is it plenum rated. - 08/28/04 03:27 AM
No.

-Hal
Posted By: trekkie76 Re: ENT is it plenum rated. - 08/28/04 02:16 PM
300-21(c)1.no ENT
Posted By: master44 Re: ENT is it plenum rated. - 08/29/04 02:19 AM
Thanks guys, I missed that in the code book.