I am aware two circuits are required for the kitchen gfci's (counter top). However is it required that evry other one be from the next circuit? ie

Ciruit1*******Circuit2******circuit1 **Cir2 etc

If so plese provide code ref. # thanks

Horizontal Ad
Joined: Feb 2002
Posts: 840
C
Member
No.


Peter
Joined: Jun 2003
Posts: 1,143
D
Member
We've run them where each side of the kitchen with a counter space (east, north) has it's own 20A GFCI circuit, including a separate one for an island, if present.

There is no requirement for "staggering" the circuitas.

Joined: Apr 2004
Posts: 42
S
Member
if i remember correctly the alaska builders code requires the staggering of the kit rec, local building code here is talking about it in the indavidual town.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,443
Joined: July 2002
Top Posters(30 Days)
Popular Topics(Views)
340,084 Are you busy
265,525 Re: Forum
246,539 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5