Kennyvp Offline OP
Member
I am aware two circuits are required for the kitchen gfci's (counter top). However is it required that evry other one be from the next circuit? ie

Ciruit1*******Circuit2******circuit1 **Cir2 etc

If so plese provide code ref. # thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2002
Posts: 840
C
Member
No.


Peter
Joined: Jun 2003
Posts: 1,143
D
Member
We've run them where each side of the kitchen with a counter space (east, north) has it's own 20A GFCI circuit, including a separate one for an island, if present.

There is no requirement for "staggering" the circuitas.

Joined: Apr 2004
Posts: 42
S
Member
if i remember correctly the alaska builders code requires the staggering of the kit rec, local building code here is talking about it in the indavidual town.