ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

5 Plug Outlet
1928 5 Plug Outlet

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 133 guests, and 21 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
Is this service correct?

[Linked Image]

[Linked Image]

No mains at meter, no mains at panels, 24 throws of the hand to kill the whole building.


[This message has been edited by iwire (edited 05-23-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Horizontal Ad
Joined: May 2001
Posts: 552
T
Member
Not around here!


Donnie
Joined: Jan 2004
Posts: 10
K
Member
Violation...Art 230.70

Frank

Joined: Feb 2002
Posts: 840
C
Member
Is this another trick question Bob? [Linked Image]

I say yes, it is correct, as long as the panels contain less than 6 breakers each.

More than that, and the panels need to be changed to main breakers. With all those new wires hanging there, that looks like what you are going to do.

Peter


Peter
Joined: May 2002
Posts: 1,716
R
Member
It is Legal. Frank look at 230.71 and take note of the wording "six sets of circuit breakers" [Linked Image]

Roger

Joined: Apr 2002
Posts: 558
C
Member
I realize that the discussion is about the number of service disconnects but……..
What size are the circuit breakers in the panels? It looks like most of them are single pole so these would be lighting and appliance panels 408.14(B). If so they wouldn’t comply with 408.16(A). Exception 2 does permit this for existing installations but these services don’t look very old.


Curt Swartz
Joined: Jan 2004
Posts: 10
K
Member
So you'll telling me that each panel doesn't need a main disconnecting means. I'm finding this very hard to accept.

What about Art. 230.79 (D) All other installations (multi-family) shall have a service disconnecting means rating of not less than 60 amperes.

Frank

Horizontal Ad
Joined: Jun 2003
Posts: 1,143
D
Member
I second the motion...

[ghettoEC] WHERE MY MAINS AT!!!! YOU DOWN WITH OCP? YOU GO, EC![/ghettoEC]

Joined: Apr 2003
Posts: 139
B
Member
I don't see how the term "sets" applies to this example. It's been my understanding that the term "sets" was added to allow multiple single pole brekers to be handle tied into one switch. (ROP 4-117, 4-118 and ROC 4-69)

As far as the original question goes, I don't see how this installation is permitted. I only see one service. There may be 4 service entrance conductors supplying 4 separate service enclosures, but I don't think the additional service entrances meet any of the exceptions to section 230.40 permitted by 230.71(A). Exception #2 could be used for the the multiple sets of service entrances, but is not allowed to be used for the purposes of 230.71(A) requirments. I feel its a violation unless someone can show otherwise.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Apr 2002
Posts: 558
C
Member
Frank,

230.71 permits more than one service disconnect. 230.80 permits the combined rating of multiple disconnects to be used to comply with 230.79.

Curt


Curt Swartz
Page 1 of 3 1 2 3

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
Popular Topics(Views)
347,089 Are you busy
272,200 Re: Forum
252,559 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5