#88155 05/15/04 02:04 PM
Joined: Apr 2001
Posts: 84
D
donles Offline OP
Member
Do I read this article correctly? In a residence, a common disconnect is not required if the circuits do not terminate on the same device or yoke. IOW, I can run 12/3 from two adjacent breakers in the panelboard to a j-box, then split off into two separate 12/2 runs for small appliance circuits? I bet alot of elec's use common trip breakers anyway.
Don

Work Gear for Electricians and the Trades

Workgear for Electricians

#88156 05/15/04 02:19 PM
Joined: May 2002
Posts: 1,716
R
Member
Your interpretation is correct except it can also apply to "other" than Dwelling Units, see 210.7(C). The key here is, if we are using a "Multi-Wire circuit it is only one circuit. [Linked Image]

Also the breakers do not have to be ajacent to one another, they only have to be on different legs or phases.

Roger