D
donles Offline OP
Member
Do I read this article correctly? In a residence, a common disconnect is not required if the circuits do not terminate on the same device or yoke. IOW, I can run 12/3 from two adjacent breakers in the panelboard to a j-box, then split off into two separate 12/2 runs for small appliance circuits? I bet alot of elec's use common trip breakers anyway.
Don

Horizontal Ad
#88156 05/15/04 02:19 PM
Joined: May 2002
Posts: 1,716
R
Member
Your interpretation is correct except it can also apply to "other" than Dwelling Units, see 210.7(C). The key here is, if we are using a "Multi-Wire circuit it is only one circuit. [Linked Image]

Also the breakers do not have to be ajacent to one another, they only have to be on different legs or phases.

Roger


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Top Posters(30 Days)
Popular Topics(Views)
352,139 Are you busy
275,935 Re: Forum
255,481 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5