210.4 #88155 05/15/04 01:04 PM
Joined: Apr 2001
Posts: 83
D
donles Offline OP
Member
Do I read this article correctly? In a residence, a common disconnect is not required if the circuits do not terminate on the same device or yoke. IOW, I can run 12/3 from two adjacent breakers in the panelboard to a j-box, then split off into two separate 12/2 runs for small appliance circuits? I bet alot of elec's use common trip breakers anyway.
Don

2017 / 2014 NEC & Related Books and Study Guides
Re: 210.4 #88156 05/15/04 01:19 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Your interpretation is correct except it can also apply to "other" than Dwelling Units, see 210.7(C). The key here is, if we are using a "Multi-Wire circuit it is only one circuit. [Linked Image]

Also the breakers do not have to be ajacent to one another, they only have to be on different legs or phases.

Roger


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,632
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,231 Are you busy
206,119 Re: Forum
194,112 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3