#87925 05/04/04 01:35 PM
Joined: May 2004
Posts: 1
C
coulomb Offline OP
Junior Member
I would like to install underground wiring along a long curved driveway for very low profile light fixtures (path lighting). I don't want to stub up PVC 90 degree ells into above ground junction boxes. Can PVC
"T" fittings be buried and used as junction
boxes? What are my code approved options here? The driveway is 250 feet long and the fixtures will be 25 feet apart. Thanks!

Work Gear for Electricians and the Trades

Workgear for Electricians

#87926 05/04/04 02:25 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
You really can not bury J-boxes or conduit bodys ("T"s)

Quote
314.29 Boxes and Conduit Bodies to Be Accessible.
Boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.

Exception: Listed boxes shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation.

The exception gives you a little leeway , but the box will have to be listed for direct burial.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#87927 05/04/04 04:59 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
That is darn little leeway, I can only think of one type of box that is listed for being installed in the ground & it is large & expensive.

How about Type UF cable? UF could be run up a post. There is a non-metallic post on the market that will conceal the cable where it comes up and the fixture can attach right to the post & it is available in a fairly low profile.

Tom


Few things are harder to put up with than the annoyance of a good example.