0 members (), 587 guests, and 17 robots.
#87343 02/16/04 03:35 PM
Y
Where do I find a Chart giving full load amps for 4160 volt mtrs. from say 100hp to 1000 hp???
Workgear for Electricians
#87344 02/16/04 06:30 PM
For 4000V motors [usual nameplate for motors used in 4160V systems] you could use 58% of the 2300V column currents in NEC Table 430-150 3ø Motor Full-Load Current (60-500hp.) Or, using the kVA/hp equivalent, a 100hp 4kV motor would be about 14½ amps and a 1,000hp motor would be ~144 amps.
#87345 02/17/04 03:42 PM
Y
I've always used .14 times Hp. But wondered if theres a chart I could get awhole of.
#87346 02/17/04 07:59 PM
Manufacturer-specific info at www.baldor.com/pdf/brochures/BR435.pdf