You will probably only have to supply overcurrent protection on the primary side. 450.6(A) and (B) discuss a couple of instances in which secondary OCPD's are required.
They're covered in 99NEC 450-4(a) Autotransformers… Secondary overcurrent protection is generally not required, but also note when “secondary” [shunt] OCP is prohibited.