#87089 01/20/04 05:29 PM
slee Offline OP
Need some guidance please. When installing an electrical distribution system, what is the requirement for grounding the sub-panels? Are we required to drive a ground rod for each sub-panel? I think not. I've always been taught/told to bond the sub-panels to the service entrance using a grounding conductor sized for the sub-panel's feeder circuit, and the service entrance is connected to the ground rod, but I can't find the reference in the 2002 NEC. Is there one?
Any help is appreciated.
thanx
#87090 01/20/04 06:36 PM
See Article 250 for all the rules for this type of grounding.
Rick Miell
#87091 01/21/04 12:31 AM
Is the sub panel in the same building?
Is it fed with a metalic conduit?
If yes, yes, your done.
If yes, no, Pull a equipment ground sized to 250.122, and do not bond the neutral to the ground in the sub panel.
Terminate the EGC to a lug or ground bar bonded to the panel