Posted By: slee grounding sub-panels - 01/20/04 09:29 PM
Need some guidance please. When installing an electrical distribution system, what is the requirement for grounding the sub-panels? Are we required to drive a ground rod for each sub-panel? I think not. I've always been taught/told to bond the sub-panels to the service entrance using a grounding conductor sized for the sub-panel's feeder circuit, and the service entrance is connected to the ground rod, but I can't find the reference in the 2002 NEC. Is there one?

Any help is appreciated.

thanx
Posted By: rmiell Re: grounding sub-panels - 01/20/04 10:36 PM
See Article 250 for all the rules for this type of grounding.

Rick Miell
Posted By: russ m Re: grounding sub-panels - 01/21/04 04:31 AM
Is the sub panel in the same building?
Is it fed with a metalic conduit?

If yes, yes, your done.
If yes, no, Pull a equipment ground sized to 250.122, and do not bond the neutral to the ground in the sub panel.
Terminate the EGC to a lug or ground bar bonded to the panel