If an outdoor residential spa has a built in GFI, does it need a GFI breaker at the Panel feeding it? Does it need a disconnect near the spa when the panel is not in with site?
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Dec 2003
Posts: 18
Member
|
according to 680-40 for outdoor spas it sends you to 680 parts A and B. 680-12 states that a disconnecting means shall be provided and accessible within sight of all pools, spas, and hot tubs and shall be at least 5 feet from the wall. As for the gfi requirement, in my area a gfci breaker is required but I cant find the article. I dont know if this is a local thing or in the nec. hope this helps.
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
Yeah, I couldn't find the GFI requirement either. Thanks for your help.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
Check out 680.44. If I'm not mistaken, a listed spa package with integral GFCI protection is permitted without GFCI protection on the branch circuit or the outlet serving the spa.
Earl
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
the disco is something that needs to be within sight of the motor, as some tub motors are not intergral to the tub ( as in commercial settings) an E-stop for the serving motor is to be placed within sight of the tub. (from the hip, this might be 680.41)
isn't it interesting that , a permanent hardwired pool should not require a GFI , where most hot tubs & spas are listed for them?
must be something to do with the bonding eh?
~S~
|
|
|
|
Joined: Aug 2001
Posts: 545
OP
Member
|
Yep, you would think an in-ground pool would need a GFI for the pump motor. The pool light has one.
The Golden Rule - "The man with the gold makes the rule"
|
|
|