A customer has rented space in a single story building with 3 spaces. Each space has 1600 sq. ft. and is seperated by a lathe and plaster wall. His architect says the seperating walls have a 4 hour fire rating and the space can be wired with romex. Any thoughts on this?thanks
 bob
 |  |  |  
| 
| 
|  |  
| 
Joined:  Jun 2001 Posts: 642 Member |  
| 
I would check with the AHJ for the area. 
 ed
 |  |  |  
| 
| 
|  |  
| 
Joined:  Aug 2003 Posts: 1,374 Moderator |  
| 
With the exception of an assembly area, you should be fine with type NM cable.
 As NEsaprky said, though, check with the AHJ
 
 Ryan Jackson,
 Salt Lake City
 |  |  |  
| 
| 
|  |  
| 
Joined:  Jan 2001 Posts: 1,044 Member |  
| 
Also keep in mind that if there will be a dropped ceiling, NM cable would not be allowed above the ceiling as open runs. 
 Few things are harder to put up with than the annoyance of a good example.
 |  |  |  
| 
| 
|  |  
| 
Joined:  Aug 2002 Posts: 141 
 OP Member |  
| 
I called the AHJ and romex it is. No dropped ceiling but thank you for the reminder. bob
 |  |  |  
| |
 | 